UPS15-58FC, 3-Speed Circulator Pump, 1/25 HP, 115 volt Zoom
  • 360° View

UPS15-58FC, 3-Speed Circulator Pump, 1/25 HP, 115 volt

SKU:59896341

Brand: Grundfos

Grundfos
Qty Price
$85.65
/ each
$335.80 / box (4 units x $83.95)
In Stock! Ships in 24-48 Hours
(743 Available)
2

Resources

Specs

Application: Zoning
Material: Cast Iron
Voltage:
?
115v
Max Pressure (PSI): 145 psi
Type: 3-Speed Pump
Features: Integral Check Valve
Horse Power:
?
1/25
Max Flow (GPM): 17
Flow Range (GPM): 0-17
Max Head (Ft): 19.5
Head Range (ft.): 0-19.5
Hertz: 60
Phase: 1
RPM: 2450
Temperature Range (F): 36°-230°F
Connection Size: 1-1/2"
1"
3/4"
1-1/4"
Connection Type: Flanged

Description for Grundfos 59896341

Grundfos UPS15-58FC circulator pump (Grundfos# 59896341) incorporates a cast iron housing, three speed motor (Low/Med/High) and a built-in, removable check valve. Grundfos UPS15-58FC is among the most popular and most versatile circulator pump models on the market. Pump's performance parameters cover nearly all traditional heating applications - from radiant and baseboards, to fan coils and zoning and many others. 3 speeds allow to set up the circulator pump in a way, that matches the system's requirements, while wet rotor design allows it to be virtually silent while operating.

Features:

  • Built-in motor protection for longer life and better performance.
  • Suitable for a wide range of applications, including radiant heating, hydronic heating, fan coil heating,
  • solar and other system types.
  • Whisper-quiet operation for sound sensitive installations.
  • Includes (2) Gaskets (O-rings).
  • UL/CSA listed.


Applications:
  • Closed loop radiant heating & snow melting systems.
  • Baseboard/Radiator/Fan coil heating and other hydronic heating applications.

UPS15-58FC, 3-Speed Circulator Pump, 1/25 HP, 115 volt

REVIEW SNAPSHOT®

by PowerReviews
GrundfosUPS15-58FC, 3-Speed Circulator Pump, 1/25 HP, 115 volt
 
4.8

(based on 75 reviews)

Ratings Distribution

  • 5 Stars

     

    (64)

  • 4 Stars

     

    (9)

  • 3 Stars

     

    (1)

  • 2 Stars

     

    (0)

  • 1 Stars

     

    (1)

99%

of respondents would recommend this to a friend.

Most Liked Positive Review

 

Great Product [...]

The radiant heat in my home is provided by hot water circulated by two Grundfos UPS15-58FC pumps, and there can be times when these seem to run for hours on end. When I...Read complete review

The radiant heat in my home is provided by hot water circulated by two Grundfos UPS15-58FC pumps, and there can be times when these seem to run for hours on end. When I installed my system, I purposely ordered three of these so that I would have a back-up in the event of an emergency. Well, I am not always the most brilliant person in the world; however, this did prove to be a wise idea. For some reason, one of the first two did fail near the end of the winter. These things can happen. In less than twenty-minutes, I switched out the bad and switched in the good, and the zone was back in business without losing any heat. The next day, I contacted Pex Supply with my warranty information, and a new replacement arrived without issue. Nothing critical has happened since, but I am prepared if it does. Meanwhile, we remain efficiently toasty throughout the cold season here on Cape Cod.

VS

Most Liked Negative Review

 

At this point not impressed

I bought this pump as a spare so I will be evaluating the one I bought in June, 2011. I am using the pump on my home hot water heating system. After installing...Read complete review

I bought this pump as a spare so I will be evaluating the one I bought in June, 2011. I am using the pump on my home hot water heating system. After installing the pump in June it seemed to work fine. When the heating season started this fall I put the pump on the low setting and it was quite for a few weeks then started to squeak. When I turned it to medium the squeaking stopped so I let it run on medium. In mid December it started to squeak on medium so I turned it to the high setting. It now only squeaks when it starts or stops but does whine(not loud) when running. It still works but at this point I am disappointed. My brother has a pump like mine only it is a single speed and he loves his.

Reviewed by 75 customers

Sort by

Displaying reviews 1-10

Back to top

Previous | Next »

 
5.0

http://www.supplyhouse.com/Grundfos-5989

By CDC

from Syracuse N.y

Verified Buyer

Comments about UPS15-58FC, 3-Speed Circulator Pump, 1/25 HP, 115 volt:

Easy To install

 
5.0

Great company with great products

By Mule

from Lehighton, Pa

Verified Buyer

Comments about UPS15-58FC, 3-Speed Circulator Pump, 1/25 HP, 115 volt:

Great product and great company

 
5.0

Needed offset flange

By Rusty the electrician.

from Manchester, NH

Verified Buyer

Comments about UPS15-58FC, 3-Speed Circulator Pump, 1/25 HP, 115 volt:

I needed a circulator with the flange 90 degrees to the motor housing so this was perfect. I like the three speeds as I can pick one that suits the application. It is easy to wire. Be aware that the housing is threaded for the electrical connector which may have to be installed before mounting this circulator at the boiler manifold. The shipping is very prompt

 
5.0

works great

By Warren

from Wilmington DE

Verified Buyer

Comments about UPS15-58FC, 3-Speed Circulator Pump, 1/25 HP, 115 volt:

have a 6ft head, works great for my 800 sqft (4 zone)radiant floor.

 
5.0

would recamend this product to a freind

By Vern

from Marcelus N Y

Verified Buyer

Comments about UPS15-58FC, 3-Speed Circulator Pump, 1/25 HP, 115 volt:

I have solar hot water for all my needs. I don't have a hot water heater. I also have radiant heat where I use three of these grundfos pumps. one is for circulating the water through the solar collectors and the other two for circulating water through the radiant heat tubes. These are one of the greatest pumps made.

 
5.0

Perfect as described.

By Al the pal

from Blaine, WA

Verified Buyer

Comments about UPS15-58FC, 3-Speed Circulator Pump, 1/25 HP, 115 volt:

Used this pump in hydronic heating system and fit right in, works perfect.

 
5.0

This is the new standard in circulators

By MM on LI

from Melville, NY

Verified Buyer

Comments about UPS15-58FC, 3-Speed Circulator Pump, 1/25 HP, 115 volt:

I have three of these on my own system and just installed two on a customers boiler refit. The small size, easy wiring and adjustable flow make these the new standard for hot water heat. From the low setting which is almost silent to the high setting which is barely a hum, these are super quiet. The three settings give a huge flow range with good ratings for head loss, far beyond what a single speed circ will give you. Grundfos has been around for a long time with a good track record. For the same price as similar rated Taco pumps, the multi speed adjustability can't be beat. With a single speed circ, you will always be a little off from the specified flow requirements of your system, either too high or two low. With this little wonder a flick of the switch increases or decreases the flow to better match what you need. Best circulator on the market for residential or light commercial hydronic system

 
5.0

Beyond Expectation

By Curtis

from Zanesville, Ohio

Verified Buyer

Comments about UPS15-58FC, 3-Speed Circulator Pump, 1/25 HP, 115 volt:

After a lengthy research process, I reluctantly chose this pump to replace my old 100 series B&G. From what I can tell this pump appears to be working better than the series 100 that it replaced. I currently have it set on speed 2 and I can't tell its running with more comfort in the zone in which it controls. I used to hear my old B&G pumping away but now all I hear is the relay kicking on. I plan on replacing my other 3 series 100 with these pumps as soon as possible.

 
5.0

I would buy this product again and again

By Paulo

from Sullivan, Wi

Verified Buyer

Comments about UPS15-58FC, 3-Speed Circulator Pump, 1/25 HP, 115 volt:

It worked right out of the box, easy to install and wire up.

 
5.0

Worked for meperfect

By Henry K

from Dallas PA

Verified Buyer

Comments about UPS15-58FC, 3-Speed Circulator Pump, 1/25 HP, 115 volt:

One zone in my House was not working perfectly.
With this item on speed 3 a quarter of my house gets instantly radiant heat. Perfect for me.

Displaying reviews 1-10

Back to top

Previous | Next »

Q&A: Ask the Questions, share answers

Do you have questions about this product?

get answers from real customers and in-house experts with AnswerBox.

55 Questions | 135 Answers
Displaying questions 1-10Previous | Next »
  • UPS15-58FC, 3-Speed Circulator Pump, 1/25 HP, 115 volt

    Q:

    I have a UPS15 58 FRC servicing 2 zones of baseboard heat. In order to get proper circulation, the control had to be set on high. Can this setting be used as a run setting, or must it be reduced to medium for regular operation?
    Asked on 1/4/2014 by Joe from Guilford CT

    8 answers

    • A:

      It's fine until it's not fine. Max flow thru 3/4" Type M copper tube is 6 gal/min. Higher than that erodes the tube. Flow should be 1 to 4 gal/min. You have unequal length zones. When sys. is running most of the water and heat flows thru the shorter zone. Running on Hi may exceed the flow rate thru the shorter zone, eroding the tube. Put in a Caleffi Circuit Balancing Valve on the short zone and set it between 1 to 4 gal min. Then adjust the pump speed setting for the second zone. Excessive noise in the baseboards indicates hi flow. It's not a simple answer. You want 1 to 4 gal/min flow above the Pressure Loss (Friction Loss) of the pipe and fittings.

      Answered on 7/23/2014 by Homer from Nevada
    • VERIFIED BUYER

      A:

      It is fine to use the high setting. I have been using this setting on a couple of my UPS15-58 pumps with no problem. It just uses 7 additional
      watts of power moving from medium to high.

      Answered on 1/5/2014 by Anonymous
    • VERIFIED BUYER

      A:

      I have looked extensively for any indication that the multi-speed
      feature implies a consideration for limiting power via duty cycling,
      etc. when operating at higher settings and have found nothing. I believe
      the high speed setting (87 Watts, and less than 10% greater than the
      mid-speed setting) is the nominal performance configuration and that it
      is designed to operate continuously this way. The lower settings in the
      UPS series permit energy savings and quieter operation when the higher
      pump speed is not needed.

      Answered on 1/5/2014 by Anonymous
    • VERIFIED BUYER

      A:

      I have run mine on all 3 settings with no adverse results.The pump draws very little electricity and will not overheat.

      Answered on 1/5/2014 by Anonymous
    • VERIFIED BUYER

      A:

      Yes it is ok to run on high speed these pump are like universal pump they replace some other old pump they made one to fit all with the same flange and fit almost anywere they insert a control box with 3 speed to be able to run the application were it use you can check on owner manual to see the pressure you nned depend on the pump curve capabality but if it work well on hight speed let it on and enjoy the heat ..!!!!!

      Answered on 1/4/2014 by theone from canada
    • VERIFIED BUYER

      A:

      No problem leaving it on high if that's what works.

      Answered on 1/4/2014 by RockHillJR from New Mexico
    • VERIFIED BUYER

      A:

      I have two out of six that I run on high and have not had any problems after 2 years. Just make sure you bleed all the air out of system,  as that causes folks a lot of problems with the circulation. 
      Sent from Jeff by mobile

      Answered on 1/4/2014 by Anonymous
    • VERIFIED BUYER

      A:

      Yes, using "High" as a run setting will be fine.
      Hazard Stewart

      Answered on 1/4/2014 by Anonymous
  • UPS15-58FC, 3-Speed Circulator Pump, 1/25 HP, 115 volt

    Q:

    What kind of warrenty does this product have?
    Asked on 12/26/2013 by Brian from Kansas

    3 answers

    • VERIFIED BUYER

      A:

      the ups15-58c has a warranty of 36 months to the original owner. covers material and workmanship of the pump. manufacture will either repair or replace defective pump. you will probably never need the warranty as this is a very good pump.

      Answered on 12/27/2013 by mike from lima, oh
    • VERIFIED BUYER

      A:

      The Grundfos circulators are designed for long life. I have a neighbor
      who has some that have been in use for many years. Here is the text from
      the included manual:
      /*Limited Warranty*
      UPS15-58 and UP15-42F circulator pumps manufactured by
      GRUNDFOS PUMPS CORPORATION (GRUNDFOS) are warranted to the
      original user only to be free of defects in material and workmanship
      for a period of 36 months from date of manufacture. GRUNDFOS'
      liability under this warranty shall be limited to repairing or replacing
      at GRUNDFOS' option, without charge, F.O.B. GRUNDFOS' factory or
      authorized service station, any UPS15-58 or UP15-42F circulator pump.
      GRUNDFOS will not be liable for any costs of removal, installation,
      transportation, or any other charges which may arise in connection
      with a warranty claim./

      Answered on 12/26/2013 by Anonymous
    • VERIFIED BUYER

      A:

      3 years

      Answered on 12/26/2013 by theone from canada
  • UPS15-58FC, 3-Speed Circulator Pump, 1/25 HP, 115 volt

    Q:

    I have this pump for baseboard zone heating system. The heat is working fine but since last few days it is making rattling noise.The noise level change with pump speed.
    Since pump is working fine, what could cause for this noise? Do I need to replace the pump or any parts?
    Asked on 12/8/2013 by rahman

    8 answers

    • VERIFIED BUYER

      A:

      the noise is usuaaly air in the system, however it can also be caused by verycold water hitting the hot boiler coils, this can ne rectified by lowerng boiler temperature, or installing a mising valve to mix some of the boiler water with the return water, thus raising the teemp of the input water to the boiler.
      This situation will arise in colder weater, and will be less prevalent in warme(less severe temps)

      Answered on 12/11/2013 by Anonymous
    • VERIFIED BUYER

      A:

      Hi no you have some air trap in the pump you will need to purge the air in it and dovit soon because youbwill break the pump

      Answered on 12/8/2013 by theone from canada
    • VERIFIED BUYER

      A:

      I don't have an answer. This is the third winter for the pump in my home
      and it is quiet.

      Answered on 12/8/2013 by Anonymous
    • VERIFIED BUYER

      A:

      Sounds like its time for a new pump ,but I would make sure its not air locked
      and running dry.

      Answered on 12/8/2013 by Anonymous
    • VERIFIED BUYER

      A:

      Try bleeding the system of air. Also, inspect your piping for loose supports, clamps etc. Can you locate or even pinpoint the location of the rattle?
      Ed Siemer
      Finish Right LLC

      Answered on 12/8/2013 by Anonymous
    • VERIFIED BUYER

      A:

      hard to say. could be defective pump or some kind of vibration. also could be air in the system which sounds like a rattle when pump runs. has anything changed that would have let air into the system? try purging the line of air to see if that helps.

      Answered on 12/8/2013 by John from New York State
    • VERIFIED BUYER

      A:

      You could have air in the system.

      Answered on 12/8/2013 by Anonymous
    • VERIFIED BUYER

      A:

      Hard to say from a distance. Could it be air in the lines? That's
      unlikely if you haven't opened the system and the pressure is maintaining
      at the recommended 12 PSI. If the pump is truly "rattling" there's a bad
      bearing or loose impeller. I'd monitor it and if it gets worse, fix it.

      Answered on 12/8/2013 by RockHillJR from New Mexico
  • UPS15-58FC, 3-Speed Circulator Pump, 1/25 HP, 115 volt

    Q:

    I have a UPS15-58 FC PN:59896769

    Are all UPS15-58 FC pumps the same as far as flange size etc?
    Under type mine says 1 PH
    Asked on 11/26/2013 by Steve

    6 answers

    • VERIFIED BUYER

      A:

      I beleive so - the absoute best flange system is the Webstone isolator uniflange ball valve - they come in pairs.Item #50403 -- Tey facilitate removal of the pump without draing the boiler or losing a lot of fluid.

      Answered on 12/11/2013 by Anonymous
    • VERIFIED BUYER

      A:

      kind of a tricky question. all ups-58 pumps are the same as far as the flange. just order the flange out let according to your pipe size. 3/4 in. thru 1-1/2. the ph just means ( single phase). 120 volt single phase.

      Answered on 12/4/2013 by mike from lima, oh
    • VERIFIED BUYER

      A:

      Look at the specs for this pump. 3/4" - 1 1/4" pipe can be adapted to it depending on the flange size you choose. If you are using 3/4" pipe get the 3/4" flange kit; 1" pipe use the 1" flange kit; etc.

      Answered on 11/27/2013 by Anonymous
    • VERIFIED BUYER

      A:

      Yes.
      Thank you!

      Answered on 11/27/2013 by Anonymous
    • VERIFIED BUYER

      A:

      What is important is, if replacing a pump already installed what is there now, as there may be something odd. In most instances flanges can be interchanged.

      Answered on 11/27/2013 by Anonymous
    • VERIFIED BUYER

      A:

      Yes the flanges are standard and will also fit Taco pumps as well as B&G pumps

      Answered on 11/26/2013 by Anonymous
  • UPS15-58FC, 3-Speed Circulator Pump, 1/25 HP, 115 volt

    Q:

    Is this pump good for out door wood furnaces? My lines come from the outdoor furnace into the basement and are horzontal to the coil in my oil furncae.
    Asked on 11/11/2013 by no nickname

    2 answers

    • VERIFIED BUYER

      A:

      It will work fine as long as the pump is not exposex to the outside elements. 
      Sent from my Galaxy S®III

      Answered on 11/11/2013 by Ben from Minnesota
    • VERIFIED BUYER

      A:

      This pump can not be installed outdoors , it can be installed horizontal with some limitations that you will see on the instructions provided with the pump.

      Answered on 11/11/2013 by Anonymous
  • UPS15-58FC, 3-Speed Circulator Pump, 1/25 HP, 115 volt

    Q:

    WILL THIS PUMP FIT INTO THE SPACE THAT IS CURRENTLY OCCUPIED BY A TACO 007 F5? ARE THE FLANGES COMPATABLE TO THE TACO FLANGES?
    Asked on 7/11/2013 by STEVE from JUNEAU AK

    2 answers

    • VERIFIED BUYER

      A:

      Yes, this is a direct replacement for a Taco 007, and in my opinion, a
      much better pump. I replaced a Taco 007 with one of these in my dad's
      house because I needed a pump with a higher head pressure so the hot
      water would reach the baseboards on the second floor. It works great
      there.
      Mark

      Answered on 7/12/2013 by Anonymous
    • CUSTOMER CARE

      A:

      This circulator has the same flange-to-flange dimensions as a Taco 007 and it works with the same flanges. Note that the direction of the motor would be different unless you have a rotated-flange 007.

      Answered on 7/15/2013 by PexSupply Staff from NY
  • UPS15-58FC, 3-Speed Circulator Pump, 1/25 HP, 115 volt

    Q:

    Further to my previous question "can this pump be manually stopped": why the pump seems to have stopped if I turn the dial and let it stay between lo and med or between med and hi? I'm pretty sure the pump stopped. And if I turn it to any of lo/med/hi, the pump started to run again.

    Does it do it any harm if the speed is manually adjusted that way ?
    Asked on 5/16/2013 by z

    2 answers

    • VERIFIED BUYER

      A:

      Hello
      U won't harm the pump doing this but it may harm the switch and capacitor if done repeatedly
      Sent from my iPad

      Answered on 5/16/2013 by Anonymous
    • VERIFIED BUYER

      A:

      Shouldn't turn the dial well under load or power not good for the motor on the pump..

      Answered on 5/17/2013 by Anonymous
  • UPS15-58FC, 3-Speed Circulator Pump, 1/25 HP, 115 volt

    Q:

    Can the pump be manually stopped? It seems possible by turning the dial between lo and medium or between medium and high speed.
    Asked on 5/15/2013 by Zhong

    4 answers

    • VERIFIED BUYER

      A:

      en> The only way to manually stop this pump is to disconnect the power.
      I have about a dozen of these in my system. I placed simple switches on
      some of them that I wanted to be able to stop without shutting down the
      entire system.

      Answered on 5/16/2013 by Anonymous
    • VERIFIED BUYER

      A:

      Personally I would install a off/on switch. Or GFI, or Power strip with off / on switch. Since the Pump only runs on 120 volts AC. Hope this helps you!!.

      Answered on 5/16/2013 by Anonymous
    • VERIFIED BUYER

      A:

      Never tried this means to manually turn pump off and would not suggest it.  Contacts inside pump speed change switch are of a "sliding" nature and might make weak contact causing a hot spot in the switch and a burn-out.  You are best to simply unplug the pump or power off its control source.

      Answered on 5/16/2013 by Anonymous
    • VERIFIED BUYER

      A:

      It's best to have the pump on a switched circuit. Using the speed switch to shut off the pump is not advisable. It's not designed to turn on or off the pump.

      Answered on 5/20/2013 by Anonymous
  • UPS15-58FC, 3-Speed Circulator Pump, 1/25 HP, 115 volt

    Q:

    I would like to know how to manually turn the pump - UPS15-58 FC. There is no slot to put the screwdriver. The furnace/boiler that it is attached to was just in a flood courtesy of Sandy. I managed to get the pilot on, but the pump is not circulating - I heard humming though. I shut it to prevent burning it out. Any help would be appreciated. We're still cleaning up after Sandy and I would like to get the heat on. Thank you.
    ...Lorraine
    Asked on 11/6/2012 by Rainey from Little Ferry NJ

    3 answers

    • CUSTOMER CARE

      A:

      This circulator requires electricity to operate. It's possible that the control that signals the pump to come on was damaged in the storm.

      Answered on 11/20/2012 by PexSupply Staff from NY
    • VERIFIED BUYER

      A:

      More information would be helpful. Do you have a pressurized system?Sounds like you have airlock. I would try this first. Open the pressure release valve on the boiler and let the air out until water comes out. With the system off and cooled down you might have to do this a couple times until the air is bled out.
      These pumps don't actually push water so any air in the system causes the water to not circulate.

      Answered on 11/7/2012 by Anonymous
    • A:

      Wow! You can't do it without removing the motor from the volute. The pump is in a closed system and the storm shouldn't have gotten into the piping. However electrical on the outside could be water damaged. If you had 220V in the house wiring due to the storm (this could happen outside of your house on the power lines) you could have serious damage to electrical parts. A complete inspection by a professional is mandatory for any heating system that has been flooded.

      Answered on 11/26/2012 by Homer from Nevada
  • UPS15-58FC, 3-Speed Circulator Pump, 1/25 HP, 115 volt

    Q:

    If the ups15-58fc pump is mated with the dielectric isolation valve set, 96806136, which comes with flat epdm seals, are both sets of gaskets used? i.e the flat seals and the ring gaskets that come with the pump.
    Asked on 10/24/2012 by Patrick from Seattle

    5 answers

    • VERIFIED BUYER

      A:

      I would use only one , the one that makes the best contact with both surfaces.

      Answered on 10/25/2012 by Anonymous
    • VERIFIED BUYER

      A:

      I would just use the large o-ring on the pump. It should compress adequately against the flat surface of the valve set.
      Hal
      Sent from my iPad

      Answered on 10/26/2012 by Anonymous
    • VERIFIED BUYER

      A:

      do not use more than one set of seals. use whatever you think will seal
      the best. one or the other, not both.

      Answered on 10/27/2012 by Anonymous
    • VERIFIED BUYER

      A:

      I used the flat ones but I would guess that you could use either or but not both. You will have a extra set. If you look at the matting surface on the pump it should be flat.

      Answered on 10/28/2012 by Anonymous
    • CUSTOMER CARE

      A:

      The key thing is that you don't use both, but the literature that comes with the isolation flanges advises that you use the diamond-shaped gaskets that come with the flanges.

      Answered on 11/20/2012 by PexSupply Staff from NY
Displaying questions 1-10Previous | Next »